Hello Joseeeph,

 

Let me explain what you're looking at from an electrician's standpoint.

 

The connection in your picture is a standard C13/14 power cord connection on the other end of the power cord you will most likely find a Nema 5-15p.

This type of power cord is capable of handling a max amperage of 15 amps†.

http://i67.tinypic.com/21ot1er.jpg

 

The square connection you are talking about from AX1500i pictures on corsair's product page, is a C19/20 style connection. With a C19/20 cord you will find either a Nema 5-15p or a Nema 5-20p plug on the end.

This type of cord is capable of handling a max amperage of 20 amps†.

http://i68.tinypic.com/15xtyls.jpghttp://i63.tinypic.com/2csi1ja.jpg

 

Now lets look at the AX1500i Psu, if you max it out at ~1500 watts you would be pulling ~12.5 @ 120Volts if your home/business is only getting ~110 volts you will be pulling ~13.5 amps. This is still within the capability of a C13 to Nema 5-15p cord.

 

 

So... the connection on your psu is fine you shouldn't have any issues.

 

On a side note for you to be aware of, at 12 amps and up there is possibility of tripping a 15amp circuit breaker due to heat build up, just something to keep in mind.

 

best of luck,

Jrcobb

 

† - the wire size of power cord should be #14 awg for 15 amps and #12awg for 20 amps.

If you live in a country that doesn't use nema style plugs and receptacles you will use a C13 to (your standard) cord most likely 250v which in turn you will have lower amperage